What’s the Definition of an ‘R-20 Wall’? - GreenBuildingAdvisor (2024)

Musings of an Energy Nerd

It’s surprisingly tricky to determine what the code means by an ‘R-20’ wall

What’s the Definition of an ‘R-20 Wall’? - GreenBuildingAdvisor (1) By Martin Holladay |

    What’s the Definition of an ‘R-20 Wall’? - GreenBuildingAdvisor (2)

    More Musings of an Energy Nerd

    1. A Cluster of New Home Failures in Ontario

    2. Removing Scale From a Tankless Water Heater

    3. A New Book for Cob Builders

    4. Residential Energy Efficiency: A Look Back on the Last 25 Years

    Builders often talk about the R-value of their walls. But if a builder claims to have an R-20 wall, what does that mean?

    Building codes commonly include a table listing the minimum prescriptive R-values for walls and ceilings in different climate zones. For example, Table R402.1.1 in the 2012 International Energy Conservation Code (IECC) informs builders that the minimum prescriptive R-value for walls in Climate Zones 3, 4, and 5 is “20 or 13+5.”

    This type of table raises many questions. For example, if a builder chooses to comply with the R-20 option, how is R-20 calculated? The code provides some guidance on the issue, but not much. According to a footnote at the bottom of the table, the “first value is cavity insulation, second is continuous insulation or insulated siding, so ‘13+5’ means R-13 cavity insulation plus R-5 continuous insulation or insulated siding.”

    Complying with the code usually means installing insulation between the studs

    The code language governing the prescriptive R-value requirements has changed in recent years. If you want to know the specific language that is enforced in your jurisdiction, you’ll have to consult your local code book. For example, the prescriptive requirements in the 2009 International Residential Code (IRC) note (in section N1102.1.1), “Computed R-values shall not include an R-value for other building materials or air films.”

    A footnote to Table N1102.1 in the 2009 IRC — equivalent in most respects to the prescriptive table (Table R402.1.1) in the 2012 IECC — notes, “R-19 batts compressed in to nominal 2×6 framing cavity such that the R-value is reduced by R-1 or more shall be marked with the compressed batt R-value in addition to the full thickness R-value.” This footnote is confusing. Who should do the marking? Does this instruction mean that the builder has to mark the insulation in every stud bay? How do…

    Weekly Newsletter

    Get building science and energy efficiency advice, plus special offers, in your inbox.

    What’s the Definition of an ‘R-20 Wall’? - GreenBuildingAdvisor (7)

    Sign up for a free trial and get instant access to this article as well as GBA’s complete library of premium articles andconstruction details.

    Start Free Trial

    Already a member? Log in

    View Comments

    17 Comments

    1. What’s the Definition of an ‘R-20 Wall’? - GreenBuildingAdvisor (8)

      user-831308 | |#1

      Oh I Wish...
      Thanks for your post. I am very glad to know "it's not just me". It seems that EVERY TIME I comb through the IRC/IECC I end up with a terrible hangover.

      Given that more than just written words are "admissible" nowadays, I surely wish the code was an interactive "living model". Something where I could go on-line, plug in my project's zip code, and click at different pieces of a beautiful model which showed me what I could (and could not do.)

      Too much to ask for, I guess.

    2. What’s the Definition of an ‘R-20 Wall’? - GreenBuildingAdvisor (9)Expert Member

      ARMANDO COBO | |#2

      Code Books? What are those...
      When I teach classes, I always make a point to ask how many people owns a code book, never mind that in most municipalities is a combination of several code books. Anyways...It's usually ZERO, but now and then I'm surprised when one or two SAY they do. That applies to Builders, Architects and Designers... very few Subs take these classes.

    3. What’s the Definition of an ‘R-20 Wall’? - GreenBuildingAdvisor (10)Expert Member

      MALCOLM TAYLOR | |#3

      Armando.
      Point taken - but I think stretched a bit. I've never met or heard of an architect who didn't own a code book. They may not have been familiar with all its requirements but they have one.

    4. What’s the Definition of an ‘R-20 Wall’? - GreenBuildingAdvisor (11)Expert Member

      ARMANDO COBO | |#4

      Sorry but it's the truth
      Malcom, all the comments I make in any blog or website are 100% my experiences, no BS, lies or stretches. I just taught a class in Santa Fe with 20+ Builders and Architects, and not a single one person in that class owned a code book. Many of them read this website and they can tell if I'm "stretching" it. Same in TX, CO, KS, OK and in almost every class I've taught. Just because this is not your experience, you should not call me less than truthful.

    5. What’s the Definition of an ‘R-20 Wall’? - GreenBuildingAdvisor (12)Expert Member

      MALCOLM TAYLOR | |#5

      Armando,
      I didn't mean to imply you are liar. I simply don't understand how this can be the case. You can not function as an architect without constant access to the building code. Even for small practices only working on individual houses I don't see how it can be done. While they may have told you this for some reason, I'd be interested to see if any come forward to this website and support your assertion.

    6. What’s the Definition of an ‘R-20 Wall’? - GreenBuildingAdvisor (13)

      user-831308 | |#6

      Own vs. access
      One thing is owning a copy of the code, another thing is knowing how to quickly access information in it.

      We have a full pdf version of the 2009 IRC, but don't actually "own" the 2012. One reason in particular: http://publicecodes.cyberregs.com/icod/irc/2012/
      and our local amendments: http://permittingservices.montgomerycountymd.gov/dps/building/BuildingCodes.aspx

      Many of my books sit on the shelf, collecting dust. This is due large in-part to the my ability to access current information much more quickly on-line than finding the book, chapter, paragraph, and keyword. By the time a book is actually published, a certain amount of it is conceivably already outdated.

      Of course this method is no substitute for simply "knowing' the right answer, but I can't always trust what I "know" is actually to code anymore, due to how quickly it all changes, especially in my particular state (the only one in the Country which automatically adopts the latest code as soon as it comes out).

    7. What’s the Definition of an ‘R-20 Wall’? - GreenBuildingAdvisor (14)

      doug_horgan | |#7

      IECC does have language about slab insulation
      There is a free copy of the 2012 IECC available here:

      http://publicecodes.cyberregs.com/icod/iecc/2012/

      This section explains what is meant by slab insulation "depth". Once you get to this section it's relatively clear:

      R402.2.9 Slab-on-grade floors.
      Slab-on-grade floors with a floor surface less than 12 inches (305 mm) below grade shall be insulated in accordance with Table R402.1.1. The insulation shall extend downward from the top of the slab on the outside or inside of the foundation wall. Insulation located below grade shall be extended the distance provided in Table R402.1.1 by any combination of vertical insulation, insulation extending under the slab or insulation extending out from the building. Insulation extending away from the building shall be protected by pavement or by a minimum of 10 inches (254 mm) of soil. The top edge of the insulation installed between the exterior wall and the edge of the interior slab shall be permitted to be cut at a 45-degree (0.79 rad) angle away from the exterior wall.

    8. What’s the Definition of an ‘R-20 Wall’? - GreenBuildingAdvisor (15)GBA Editor

      Martin Holladay | |#8

      Response to Douglas Horgan
      Douglas,
      Thanks very much for providing that code reference. It's a section that I somehow missed. I'm grateful for the reference, and I have edited my article for accuracy.

      The most curious aspect of section R402.2.9 of the 2012 IECC is that it does not require any insulation for above-grade slabs. The only slabs that are required to be insulated are “Slab-on-grade floors with a floor surface less than 12 inches below grade” -- a rare type of construction.

      Most concrete slabs are either above grade (usually between 4 inches and 8 inches above grade), or are more than 12 inches below grade (for example, basem*nt slabs).

    9. What’s the Definition of an ‘R-20 Wall’? - GreenBuildingAdvisor (16)

      wjrobinson | |#9

      iECC is NOT the code every where
      NYS Code.... Is.... NYS Code.

      We modify IECC code and implement codes years later than published.

      And if code is a builders or Arch's problem then they sure must have greater issues.

    10. What’s the Definition of an ‘R-20 Wall’? - GreenBuildingAdvisor (17)Expert Member

      MALCOLM TAYLOR | |#10

      Response to Martin,
      I think you are reading it a bit too narrowly. Isn't the distinction that provision is trying to address that between slabs more than 12" below grade and all other slabs above that height?

    11. What’s the Definition of an ‘R-20 Wall’? - GreenBuildingAdvisor (18)GBA Editor

      Martin Holladay | |#11

      Response to Malcolm Taylor
      Malcolm,
      Yes, I think you've put your finger on it -- it's probably another example of the inability of code writers to write English.

      Let's see -- is there a difference between slabs that are "below grade" and slabs that are "above grade"? Why, yes -- I think there is.

      But the code writers never mentioned what to do with slabs that are above grade.

      Are these two sentences equivalent? You decide.

      1. My proposed version: "Slab-on-grade floors that with a floor surface that is above grade or that is less than 12 inches (305 mm) below grade shall be insulated in accordance with Table R402.1.1."

      2. The existing language: "Slab-on-grade floors with a floor surface less than 12 inches (305 mm) below grade shall be insulated in accordance with Table R402.1.1."

    12. What’s the Definition of an ‘R-20 Wall’? - GreenBuildingAdvisor (19)Expert Member

      MALCOLM TAYLOR | |#12

      Martin,
      Your wording would help a lot.
      Obscure code language can have much larger consequences in rural areas where most of the enforcement is done by inspectors on site when things are already built, rather than plan checking before construction starts. It also undermines client's faith in their designer when you can't guarantee that what you draw will pass inspection.

    13. What’s the Definition of an ‘R-20 Wall’? - GreenBuildingAdvisor (20)GBA Editor

      Martin Holladay | |#13

      Response to Malcolm Taylor
      Malcolm,
      If only the International Code Council would hire a few unemployed English majors, we could clarify the building code and lower the unemployment rate for liberal arts graduates.

      .

    14. What’s the Definition of an ‘R-20 Wall’? - GreenBuildingAdvisor (22)Expert Member

      MALCOLM TAYLOR | |#14

      Martin
      Send a few our up here, ours is just as bad.
      I think part of the problem is that code writers write for code writers. I changed the way I label drawings and write specifications when I realized that architects write for architects, rather than the builders and subs that have to interpret them. Much of the jargon can be replaced by plain english equivalents, and a lot of it is included just to cover our asses.

    15. What’s the Definition of an ‘R-20 Wall’? - GreenBuildingAdvisor (23)

      mbsheffer | |#15

      90.1 Appendix A
      Our work is mostly commercial and we use ASHRAE 90.1 Appendix A to determine whole assembly U-values. Not perfect but it is a pretty organized and understandable way to estimate the whole assembly performance.

    16. What’s the Definition of an ‘R-20 Wall’? - GreenBuildingAdvisor (24)

      tferrera1 | |#16

      Hangover starting
      2. The existing language: "Slab-on-grade floors with a floor surface less than 12 inches (305 mm) below grade shall be insulated in accordance with Table R402.1.1."

      I confused by your interpretation Martin. The code seems to ask that slabs near or above grade be insulated. Makes sense. That surface is colder (winter) or warmer (summer) than anything below 12". To my mind a basem*nt slab 4 or more feet below grade would need less or no insulation as that ground surface is much more moderate in temperature through the seasons than the ground surfaces closer to grade. This is the principle of geothermal energy is it not?

    17. What’s the Definition of an ‘R-20 Wall’? - GreenBuildingAdvisor (25)GBA Editor

      Martin Holladay | |#17

      Response to Tony Ferrera
      Tony,
      I'm not questioning the logic that calls for less insulation for slabs that are deeply below grade than for slabs that are near grade. That makes sense.

      What I am questioning is the confusing language of the code, which discusses the requirements for slabs that are "below grade," but which is silent on what should be done with slabs that are above grade.

    Log in or become a member to post a comment.

    Sign up Log in

    Weekly Newsletter

    Get building science and energy efficiency advice, plus special offers, in your inbox.

    Related

    • Musings of an Energy Nerd

      Understanding the Latest Energy Code

      The 2021 IECC raises the bar on insulation levels and energy performance

    • Musings of an Energy Nerd

      Vermont Addresses the 20+5 Wall Problem — Sort Of

      The 2015 Vermont energy code tries to steer builders away from exterior rigid foam that is too thin

    • Musings of an Energy Nerd

      Three Code-Approved Tricks for Reducing Insulation Thickness

      Savvy builders know that there are several legal ways to install less insulation than the minimum requirements in the prescriptive code table

    • Musings of an Energy Nerd

      What’s the Definition of ‘Green Building’?

      I’ve identified ten principles that show up in the various definitions of this tricky term

    Recent Questions and Replies

    • |

    • |

    • |

    • |

    View MoreAsk a Question

    Featured Blogs

    Musings of an Energy NerdView More

    Contemplating residential energy use

    • A Cluster of New Home Failures in Ontario

    • Removing Scale From a Tankless Water Heater

    • A New Book for Cob Builders

    Product GuideView More

    • Subfloor Sheathing

    • Insulation With Integrated WRB and/or Sheathing

    • Membrane Air Barriers

    What’s the Definition of an ‘R-20 Wall’? - GreenBuildingAdvisor (2024)

    FAQs

    What does R20 insulation mean? ›

    The R-value for insulation is a way to measure how much resistance the insulation has to heat flow. The higher the R-value, the more the resistance and the better the material is at insulating a home. Generally, insulation materials with higher R-values cost more when compared to those with lower R-values.

    What is an R rating exterior wall? ›

    Typical recommendations for exterior walls are R-13 to R-23, while R-30, R-38 and R-49 are common for ceilings and attic spaces.

    What is the R-value of a wall mean? ›

    R-value is simply a measure of a material's thermal resistance to heat flow. It is used to determine how well a material insulates. The higher the R-value, the greater the material's insulating properties.

    What does R 20 5 CI mean? ›

    Based on the example of R20 +5ci, this would entail a 2×6 exterior wall with a min cavity insulation of R20 PLUS a min of R5 of continuous insulation.

    How much does a bag of R20 insulation cover? ›

    R-20 Pink Fiberglass Insulation 15-inch x 47-inch x 6-inch. For 2"x6" walls with 16" on center stud spacing. Coverage: 78.3 square feet per bag.

    How thick is R20 rigid insulation? ›

    As you can see, the R-value of EPS rigid insulation requires increasing thicknesses and/or densities in order to achieve a good thermal barrier. For example, if you want to meet the minimum R13 for walls, you'll need at least 3” thick EPS. For an R20 wall, you'll need 4” or more, depending on the density you select.

    What is the highest R-value for a 2x4 wall? ›

    Fiberglass and rock wool batts—2x4 walls can hold R-13 or R-15 batts; 2x6 walls can have R-19 or R-21 products. Generally, batt insulation is the least expensive wall insulation material but requires careful installation for effective performance (see page 4).

    What wall insulation has the best R-value? ›

    Rigid foam board insulation is available in many materials, including polystyrene (R-3.8 to R-5.0), polyurethane (R-5.5 to R-6.5) and polyisocyanurate (R-5.6 to R-8.0). Since it has the highest R-value, rigid foam is typically reserved for foundations and basem*nt walls.

    What R-value does 1/2 drywall have? ›

    Drywall has a relatively low R-value — about 0.45 at ½” thickness. This is similar to building materials such as siding, concrete, dirt, face brick, particleboard, wood and single-pane glass.

    Can I use 2x4 insulation in a 2x6 wall? ›

    While rated differently, these two types of insulation are close enough in thickness that they can both fit in these wall systems. Older homes, especially those predating the 1950s, may employ two-by-fours with a true measurement of 2 inches by 4 inches.

    What is a good R-value for garage walls? ›

    Generally, insulation with an R-value between R-13 and R-21 is recommended. Adding insulation to exterior walls (including garage walls attached to living spaces) can help increase R-value and create a more powerful thermal boundary for your home. If you're insulating your garage ceiling, you'll need a higher R-value.

    What does R20 mean? ›

    ACH Return Code R20, also known as "Non-Transaction Account," is a standard code used in Automated Clearing House (ACH) transactions. It indicates that the entry in the ACH file is being rejected because the receiving account is not a transaction account.

    How do you increase the R-value of a wall? ›

    Installing more insulation in your home increases the R-value and the resistance to heat flow. In general, increased insulation thickness will proportionally increase the R-value.

    What is R5 insulation good for walls? ›

    Materials Used to Make R5 Insulation

    It is typically used in batt or roll form and is suitable for walls and attics. Foam board insulation, on the other hand, consists of rigid panels that provide consistent thermal resistance and are commonly used in exterior sheathing and foundation walls.

    What is the difference between R20 and R30? ›

    R20 are the most common R type LED floods you can find in many homes as they are used as recessed can lightning or track lighting. The R30 is rare because it's an old design that is getting phased out since it is less energy efficient. Instead, it's replaced with BR30 LED bulb which is interchangeable.

    What is a good R-value on insulation? ›

    The U.S. Department of Energy recommends attic insulation levels of R-49 to R-60 for most homes in colder climates, and R-30 to R-49 for homes in warmer climates.

    Is R20 for 2x6? ›

    R20 Insulation is 5.5" thick and designed to fit in 2x6 stud bays.

    How many square feet is R20 insulation? ›

    Description. This Johns Manville R20 fibreglass building insulation is formaldehyde free, fireproof and mould resistant. It provides effective resistance to heat transfer. It is 15 x 47 x 6 inches in size with a coverage area of 78.33 square feet.

    Top Articles
    Latest Posts
    Article information

    Author: Domingo Moore

    Last Updated:

    Views: 5935

    Rating: 4.2 / 5 (73 voted)

    Reviews: 80% of readers found this page helpful

    Author information

    Name: Domingo Moore

    Birthday: 1997-05-20

    Address: 6485 Kohler Route, Antonioton, VT 77375-0299

    Phone: +3213869077934

    Job: Sales Analyst

    Hobby: Kayaking, Roller skating, Cabaret, Rugby, Homebrewing, Creative writing, amateur radio

    Introduction: My name is Domingo Moore, I am a attractive, gorgeous, funny, jolly, spotless, nice, fantastic person who loves writing and wants to share my knowledge and understanding with you.